An ideal transformer with purely resistive load operates at 12 kV on the primary side. It supplies electrical energy to a number of nearby houses at 120 V. The average rate of energy consumption in the houses served by the transformer is 60 kW. The value of resistive load (Rs) required in the secondary circuit will be .

Answer: 240

Solution

For an ideal transformer, power is conserved: kW. The secondary voltage is V, so the secondary current is A. The resistive load in the secondary is .

JEE Main · 2023 · 06 Apr 2023 · Shift 1 · Integer answer

More JEE Main questions on Alternating Current

  1. Using a variable-frequency a.c. voltage source, the maximum current measured in the given LCR circuit is 50 mA for . The values of L and R are shown in the figure. The capacitance of the capacitor (C) used is ______ F.
    JEE Main 2026View solution →
  2. For the series LCR circuit connected with 220 V, 50 Hz a.c source as shown in the figure, the power factor is . The value of is
    JEE Main 2026View solution →
  3. The electric current in the circuit is given as . The r.m.s current for the period to is ______
    JEE Main 2026View solution →
  4. An inductor stores 16 J of magnetic field energy and dissipates 32 W of thermal energy due to its resistance when an a.c. current of 2 A (rms) and frequency 50 Hz flows through it. The ratio of inductive reactance to its resistance is ______ .
    ( )
    JEE Main 2026View solution →
  5. The figure given below shows an LCR series circuit with two switches and . When switch is closed keeping open, the phase difference between the current and source voltage is and phase differe …
    JEE Main 2026View solution →
  6. An inductor of 10 mH, capacitor of and a resistor of are connected in series across an a.c power supply . The power factor of the given circuit is 0.5. The difference in the inductive reactance and capacit …
    JEE Main 2026View solution →